electrical connectors / al wire
Posted: Fri Feb 17, 2012 11:08 pm
Aluminum got a bad rap early on as the alloys would cold flow as well as
thermally loosen. That has been largely solved. There are some
important points however.
Use only compression lugs, either AL (tin or silver plated) or copper
rated for use on AL cable by the mfg.
Do not abrade the tin or silver plating.
Use a an electrical joint compound for aluminum such made by Burndy or
Thomas & Betts. These have a grease that excludes O2 and a zinc filler
that enhances conduction.
Use a Belleville (cup spring) washer under bolted connections.
There, that about does it. If those steps are followed you will have a
long term reliable joint. Frankly, unless there is an overriding reason
to use AL such as a long run of larger cable I would use the copper.
Ralph Baker
Elite 624E
*-------------------------------------------------------------------------*
To unsubscribe from this list go to:
http://www.dcsol.com:81/public/code/html-subscribe.wcx
Archives located at http://rebel:builder@www.dcsol.com:81/default.htm
To contact the list admin, e-mail mike.davis@dcsol.com
*-------------------------------------------------------------------------*
-----------------------------------------------------------------
List archives located at: https://mail.dcsol.com/login
username "rebel" password "builder"
Unsubscribe: rebel-builders-unsubscribe@dcsol.com
List administrator: mike.davis@dcsol.com
-----------------------------------------------------------------
thermally loosen. That has been largely solved. There are some
important points however.
Use only compression lugs, either AL (tin or silver plated) or copper
rated for use on AL cable by the mfg.
Do not abrade the tin or silver plating.
Use a an electrical joint compound for aluminum such made by Burndy or
Thomas & Betts. These have a grease that excludes O2 and a zinc filler
that enhances conduction.
Use a Belleville (cup spring) washer under bolted connections.
There, that about does it. If those steps are followed you will have a
long term reliable joint. Frankly, unless there is an overriding reason
to use AL such as a long run of larger cable I would use the copper.
Ralph Baker
Elite 624E
*-------------------------------------------------------------------------*
To unsubscribe from this list go to:
http://www.dcsol.com:81/public/code/html-subscribe.wcx
Archives located at http://rebel:builder@www.dcsol.com:81/default.htm
To contact the list admin, e-mail mike.davis@dcsol.com
*-------------------------------------------------------------------------*
-----------------------------------------------------------------
List archives located at: https://mail.dcsol.com/login
username "rebel" password "builder"
Unsubscribe: rebel-builders-unsubscribe@dcsol.com
List administrator: mike.davis@dcsol.com
-----------------------------------------------------------------